Quote:
Originally Posted by jing View Post
Bx aka armored cable aka AC90

Loomex in any conduit, metallic or non, is not allowed.
Not entirely correct.

More specifically, Non Metallic Sheathed Cable or NMD90 (Loomex) may not be used within a raceway when part of a complete raceway system.
The code does allow for NMD90 to be installed within short sections of conduit and tubing for the purposes of mechanical protection
Per CEC Section 12-910(2)