You'd have to do some cutting and patching.

Cut in and mount your new outlet boxes where you want them, open up the ceiling as necessary to pull wire through and able to staple to face of joist every 5 feet (Also need to staple within 6" of Junction Box).
If you need to move perpendicular through joists, you can drill, but ensure you keep at least 1-1/4" from edge of joist.
All splices must be made within your junction boxes.
All junction boxes must be accessible once the ceiling is closed back up (Can't bury them within the ceiling)