Not entirely correct.
More specifically, Non Metallic Sheathed Cable or NMD90 (Loomex) may not be used within a raceway when part of a complete raceway system.
The code does allow for NMD90 to be installed within short sections of conduit and tubing for the purposes of mechanical protection
Per CEC Section 12-910(2)
|
Not a sparky myself, just work with them enough to know a couple things.
@Great68 must be a city inspector being able to cite the CEC like that
OP can just post his CEC questions in here now instead of buying a code book