C02 alarm starts blaring and the fans kick in, both don't shut off until the area's clear. I think the detector is right behind the post where my exhaust is lol
|
CO, not CO2.
Yeah your tailpipe proximity to the detector could be an issue.
I've installed these gas detection systems in parkades. In all the ones I've installed we configure them for two stages at separate trip levels. Stage 1 kicks on the exhaust fans but no audible alarm, Stage 2 is the audible alarm.
Unless something has mechanically failed, like the exhaust fan failed to start, the system should never normally hit stage 2. (Or the installer never properly setup the trip thresholds)